1.

Two wattmeters are connected to measure the total power consumed by a 3-ϕ load at 0.5 power factor lagging. The total power consumed by the load as indicated by the two wattmeters is 30 kW. Find the individual wattmeter readings.

A. W1 = 10 kW & W2 = 20 kW
B. W1 = 15 kW & W2 = 15 kW
C. W1 = 5 kW & W2 = 25 kW
D. W1 = 30 kW & W2 = 0
Answer» E.