The severity of line-to-ground and three-phase faults at the terminals of unloaded synchronous generator is to be same. If the terminal voltage is 1.0 pu and Z1 = Z2 = j0. 1 pu, Z0 = j0.05 pu for the alternator, then the required inductive reactance for neutral grounding is

A. 0.0166 pu
B. 0.05 pu
C. 0.1 pu
D. 0.15 pu
Answer» B. 0.05 pu