The severity of line-to-ground and three-phase faults at the terminals of unloaded synchronous generator is to be same. If the terminal voltage is 1.0 pu and Z1 = Z2 = j0. 1 pu, Z0 = j0.05 pu for the alternator, then the required inductive reactance for neutral grounding is |
| A. | 0.0166 pu |
| B. | 0.05 pu |
| C. | 0.1 pu |
| D. | 0.15 pu |
| Answer» B. 0.05 pu | |