The positive, negative and zero sequence impedances of a three-phase generator are Z1, Z2 and Z0 respectively. For a line-to-line fault with fault impedance Zf, the fault current is If1 = kIf, where If is the fault current with zero fault impedance. The relation between Zf and k is |
| A. | \({Z_f} = \frac{{\left( {{Z_1} + {Z_2}} \right)\left( {1 - k} \right)}}{k}\) |
| B. | \({Z_f} = \frac{{\left( {{Z_1} + {Z_2}} \right)\left( {1 + \;k} \right)}}{k}\) |
| C. | \({Z_f} = \frac{{\left( {{Z_1} + {Z_2}} \right)k}}{{1 - k}}\) |
| D. | \({Z_f} = \frac{{\left( {{Z_1} + {Z_2}} \right)k}}{{1 + k}}\) |
| Answer» B. \({Z_f} = \frac{{\left( {{Z_1} + {Z_2}} \right)\left( {1 + \;k} \right)}}{k}\) | |