1. |
The frequency of the carrier in the case of carrier-current-pilot scheme is in the range of _________ |
A. | 50 kHz-500 kHz |
B. | 1 kHz-10 kHz |
C. | 25 kHz-50 kHz |
D. | 15 kHz-25kHz |
Answer» B. 1 kHz-10 kHz | |
2. |
If a transformer is provided with differentially connected relay. To prevent the mal operation of the relay, the relay restraining coil is biased with ______________ |
A. | 3rd harmonic |
B. | 2nd harmonic |
C. | 7th harmonic |
D. | 5th harmonic |
Answer» C. 7th harmonic | |
3. |
If a transformer is provided with differentially connected relay. To prevent the mal operation of the relay, the relay relay operating coil is biased with ______ |
A. | 3rd harmonic |
B. | 2nd harmonic |
C. | 7th harmonic |
D. | 5th harmonic |
Answer» E. | |
4. |
While a transformer is energised, the differentially connected relay will |
A. | mal operate |
B. | not mal operate |
C. | mal operate for lagging loads |
D. | never mal operate |
Answer» B. not mal operate | |
5. |
The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding? |
A. | 2.12 Ω |
B. | 1.12 Ω |
C. | 4.24 Ω |
D. | 3.24 Ω |
Answer» B. 1.12 Ω | |
6. |
The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults? |
A. | 76.4 |
B. | 23.6 |
C. | 73 |
D. | None of the mentioned |
Answer» C. 73 | |
7. |
The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against earth faults? |
A. | 76.4 |
B. | 77.8 |
C. | 73 |
D. | None of the mentioned |
Answer» B. 77.8 | |
8. |
The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults? |
A. | 76.4 |
B. | 77.8 |
C. | 73 |
D. | None of the mentioned |
Answer» E. | |
9. |
A three phase transformer having a line voltage ratio of 400/33000 V is connected in the star-delta. The CTs on the 400V side have a CT ratio of 1000/5. What will be the current through the pilot wire? |
A. | 5√3 A |
B. | 5/√3 A |
C. | 5 A |
D. | 1/5 A |
Answer» B. 5/√3 A | |
10. |
A three phase transformer having a line voltage ratio of 400/33000 V is connected in the star-delta. The CTs on the 400V side have a CT ratio of 1000/5. What must be the ratio of CTs on the 33000 side? |
A. | 7/5 |
B. | 5/7 |
C. | 3/5 |
D. | 5/2 |
Answer» B. 5/7 | |
11. |
The factor which influences the acr de ionisation dominantly ________ |
A. | line voltage |
B. | magnitude of transient fault current |
C. | speed of reclosure |
D. | all of the mentioned |
Answer» B. magnitude of transient fault current | |