The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding? |
A. | 2.12 Ω |
B. | 1.12 Ω |
C. | 4.24 Ω |
D. | 3.24 Ω |
Answer» B. 1.12 Ω | |