1.

The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?

A. 2.12 Ω
B. 1.12 Ω
C. 4.24 Ω
D. 3.24 Ω
Answer» B. 1.12 Ω