1.

The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against earth faults?

A. 76.4
B. 77.8
C. 73
D. None of the mentioned
Answer» B. 77.8