The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against earth faults? |
A. | 76.4 |
B. | 77.8 |
C. | 73 |
D. | None of the mentioned |
Answer» B. 77.8 | |