MCQOPTIONS
Saved Bookmarks
1. |
A three phase transformer has a name plate details of 30 MVA and voltage rating of 230Y kV/69∆ kV with a leakage reactance of 10% and the transformer connection via wye-delta. Taking a base of 230 kV on the high voltage side, the transformer reactance referred to the low voltage side in ohms is __________ |
A. | 47.61 Ω |
B. | 15.87 Ω |
C. | 176.33 Ω |
D. | 157.8 Ω |
Answer» B. 15.87 Ω | |