

MCQOPTIONS
Saved Bookmarks
1. |
A 3 phase delta/star transformer is supplied at 6000 V on the delta-connected side. The terminal voltage on the secondary side when supplying full load at 0.8 lagging power-factor is 415 V. The equivalent resistance and reactance drops for the transformer are 1% and 5% respectively. The turns ratio of the transformer is _______ . |
A. | 4 |
B. | 24 |
C. | 12 |
D. | All of the above |
Answer» C. 12 | |