A 3 phase, 10 kW, 400 V, 4 pole, 50 Hz, star connected induction motor draws 20 A on full load. Its no load and blocked rotor test data are given below : No Load test : 400V 6 A 1002 W Blocked Rotor test : 90 V 15 A 762 W Neglecting copper loss in no Load test and core loss in Blocked Rotor test, estimate motor 's full load efficiency. |
A. | 76% |
B. | 81% |
C. | 82.4% |
D. | 85% |
Answer» C. 82.4% | |