A 11 kV 100 MVA alternator is grounded through a resistance of 4 Ω. The C.T.s have a ratio of 500/5. The relay is set to operate when there is an out of balance current of 2 A. What percentage of generator winding will be protected by the percentage differential protection scheme?

A. 93.7
B. 6.3
C. 87.4
D. 84.5
Answer» D. 84.5