A 11 kV 100 MVA alternator is grounded through a resistance of 4 Ω. The C.T.s have a ratio of 500/5. The relay is set to operate when there is an out of balance current of 2 A. What percentage of generator winding will be protected by the percentage differential protection scheme? |
A. | 93.7 |
B. | 6.3 |
C. | 87.4 |
D. | 84.5 |
Answer» D. 84.5 | |