| 1. | Where severe synchronising swing occur, the relay employed is | 
| A. | Impedance relay | 
| B. | Mho relay | 
| C. | Reactance relay | 
| D. | Induction relay | 
| Answer» C. Reactance relay | |
| 2. | Requirements of protection power station buildings against direct strokes are | 
| A. | Interception | 
| B. | Conduction | 
| C. | . Dissipation | 
| D. | All of the above | 
| Answer» E. | |
| 3. | For the protection of power station buildings against direct strokes therequirements are | 
| A. | Interception | 
| B. | Interception and conduction | 
| C. | Interception, conduction and dissipation | 
| D. | Interception,conduction,dissipation and reflection | 
| Answer» D. Interception,conduction,dissipation and reflection | |
| 4. | The current zero interruption, in oil and air blast circuitbreakers, is achieved by | 
| A. | lengthening of the gap | 
| B. | cooling and blast effect | 
| C. | both (A) and (B) | 
| D. | deionizing the oil with forced air | 
| Answer» D. deionizing the oil with forced air | |
| 5. | The most efficient torque producing actuating structure for the induction typerelays is | 
| A. | Shaded pole structure | 
| B. | Watt hour meter structure | 
| C. | Induction cup structure | 
| D. | Single induction loop structure | 
| Answer» D. Single induction loop structure | |
| 6. | Differential relays are used for protection of | 
| A. | Feeders | 
| B. | Alternators | 
| C. | Transformers | 
| D. | All of the above | 
| Answer» E. | |
| 7. | Directional over current relays have two exciting coils connected across | 
| A. | CT secondaries of two different phases | 
| B. | VT secondaries of two different phases | 
| C. | CT and VT secondaries of same phases | 
| D. | CT and VT secondaries of two different phases | 
| Answer» D. CT and VT secondaries of two different phases | |
| 8. | A three phase, 33 kV oil circuit breaker is rated 1200 A, 2000 MVA, 3s. What isits symmetrical breaking current? | 
| A. | 1200 A | 
| B. | 3600 A | 
| C. | 35 kA | 
| D. | 104.8 kA | 
| Answer» D. 104.8 kA | |
| 9. | Which of the following medium is employed for extinction of arc in air circuitbreaker ? | 
| A. | Water | 
| B. | Oil | 
| C. | Air | 
| D. | SF6 | 
| Answer» D. SF6 | |
| 10. | Which among these tests are performed to check the nation or internationalstandards? | 
| A. | Type test. | 
| B. | Production tests. | 
| C. | Site checks. | 
| D. | All of the above. | 
| Answer» B. Production tests. | |
| 11. | Switching over voltage arc are more hazardous than lighting surges in case of | 
| A. | Unbalanced systems | 
| B. | Low-voltages | 
| C. | 11 KV systems | 
| D. | EHV and UHV systems | 
| Answer» E. | |
| 12. | Which type of air is used in air blast circuit breaker? | 
| A. | Ionised air | 
| B. | Air free from moisture | 
| C. | Air should have least CO2 | 
| D. | Air must have oil mist. | 
| Answer» C. Air should have least CO2 | |
| 13. | What is / are the main disadvantage / s of using oil as the quenching medium in the circuit breakers? | 
| A. | Need periodical replacement. | 
| B. | Risk of formation of explosive mixture with air. | 
| C. | Possibility of causing fire hazards. | 
| D. | All of the above. | 
| Answer» E. | |
| 14. | Why is it difficult to interrupt a capacitive circuit? | 
| A. | The current has a leading power factor. | 
| B. | The restriking voltage can be high. | 
| C. | Current magnitude is very small. | 
| D. | Stored energy in the capacitor is very high. | 
| Answer» C. Current magnitude is very small. | |
| 15. | Time graded protection of a radial feeder can be achieved by using | 
| A. | Definite time relay | 
| B. | Inverse time relay | 
| C. | Both definite and inverse time relays | 
| D. | None of the above | 
| Answer» D. None of the above | |
| 16. | An impedance is relay is a | 
| A. | Voltage restrained over current relay | 
| B. | Voltage restrained directional relay | 
| C. | Directional restrained over current relay | 
| D. | Directional restrained over voltage relay | 
| Answer» B. Voltage restrained directional relay | |
| 17. | For the protection of power station buildings against direct strokes the requirementsare | 
| A. | interception | 
| B. | interception and conduction | 
| C. | interception, conduction and dissipation | 
| D. | interception, conduction, dissipation and reflection | 
| Answer» D. interception, conduction, dissipation and reflection | |
| 18. | For the protection of lines against faults involving variable fault resistance, thepreferred relaying scheme is a | 
| A. | Plain impedance relay | 
| B. | Directional over-current relay | 
| C. | Mho relay | 
| D. | Reactance relay | 
| Answer» E. | |
| 19. | Differential relays are used for protection of equipments against | 
| A. | Internal faults | 
| B. | Over current | 
| C. | Reverse current | 
| D. | Reverse power | 
| Answer» B. Over current | |
| 20. | The least expensive protection for over current in low-voltage system is | 
| A. | Rewirable fuse | 
| B. | Isolator | 
| C. | Circuit breaker | 
| D. | Air-break switch | 
| Answer» B. Isolator | |
| 21. | In axial blast type of CB, expansion of air takes place from ______________. | 
| A. | High pressure to low pressure. | 
| B. | Low pressure to high pressure. | 
| C. | Always in high pressure. | 
| D. | Always in low pressure. | 
| Answer» B. Low pressure to high pressure. | |
| 22. | In an inverse definite minimum time, electromagnetic type over current relay, theminimum time feature is achieved because of | 
| A. | Saturation of the magnetic circuit | 
| B. | Proper mechanical design | 
| C. | Appropriate time delay element | 
| D. | Electromagnetic damping | 
| Answer» B. Proper mechanical design | |
| 23. | How is the restriking voltage measured? | 
| A. | RMS value | 
| B. | Peak value | 
| C. | Instantaneous value | 
| D. | Average value | 
| Answer» C. Instantaneous value | |
| 24. | A fuse wire of circular cross section has a radius of 0.8mm. The wire blows off at a current of 9(A) What will be the radius of the wire that will blow off at a current of 1A? | 
| A. | 0.2 mm | 
| B. | 0.18 mm | 
| C. | 0.28 mm | 
| D. | 0.3 mm | 
| Answer» C. 0.28 mm | |
| 25. | Hey switchgear is device used for | 
| A. | Interrupting an electrical circuit | 
| B. | Switching an electrical circuit | 
| C. | Reaching and controlling an electrical circuit | 
| D. | Switching, controlling and protecting the electrical circuit and equipment | 
| Answer» E. | |
| 26. | The line insulation is............. the insulation level at the station equipment | 
| A. | Less than | 
| B. | Same as | 
| C. | More than | 
| D. | Not directly related with | 
| Answer» E. | |
| 27. | What is the major cause of the failure of the circuit breaker? | 
| A. | Trip circuit open | 
| B. | Trip latch defective | 
| C. | Spring defective | 
| D. | All of these | 
| Answer» E. | |
| 28. | What is the arc voltage in a circuit breaker? | 
| A. | In phase with the arc current. | 
| B. | Lagging the arc current by 90° | 
| C. | Leading the arc current by 90° | 
| D. | Lagging the arcing current by 180° | 
| Answer» B. Lagging the arc current by 90° | |
| 29. | Both voltage and current signals are required for | 
| A. | A plain over current relay | 
| B. | A differential relay | 
| C. | A directional relay | 
| D. | A biased directional relay | 
| Answer» D. A biased directional relay | |
| 30. | In order that current should flow without causing excessive heating or voltage drop,the relay contacts should | 
| A. | have low contact resistance | 
| B. | be clean and smooth | 
| C. | be of sufficient size and proper shape | 
| D. | have all above properties | 
| Answer» E. | |
| 31. | The operating speed of a relay depends upon the | 
| A. | Rate of flux built up | 
| B. | Armature core air gap | 
| C. | Spring tension | 
| D. | All of these | 
| Answer» E. | |
| 32. | The frequency of carrier in the carrier current pilot scheme is in the range of | 
| A. | 1 kHz to 10 kHz | 
| B. | 10 kHz to 25 kHz | 
| C. | 25 kHz to 50 kHz | 
| D. | 50 kHz to 500 kHz | 
| Answer» E. | |
| 33. | What is restriking voltage? | 
| A. | The transient voltage that appears across the circuit breaker contacts at the instant of arc extinction. | 
| B. | The transient voltage that appears across the circuit breaker contacts at the end of arc extinction. | 
| C. | Both (a) and (b) | 
| D. | None of the above | 
| Answer» B. The transient voltage that appears across the circuit breaker contacts at the end of arc extinction. | |
| 34. | In a static over current relay, inverse time characteristics are obtained by | 
| A. | A transistor amplifier | 
| B. | An integrating circuit | 
| C. | A transistor switch | 
| D. | A differentiating circuit | 
| Answer» C. A transistor switch | |
| 35. | The air blast circuit breakers for 400 kV systems are designed to operate in howmuch time? | 
| A. | 0.1 s | 
| B. | 0.5 s | 
| C. | 50 ms | 
| D. | 100µs | 
| Answer» D. 100µs | |
| 36. | Why is the resistance switching used in a air blast circuit breaker? | 
| A. | Reduce the magnitude of fault current. | 
| B. | Control the CB operating time. | 
| C. | Damp out the fast transient. | 
| D. | Change the fault current power factor. | 
| Answer» D. Change the fault current power factor. | |
| 37. | The frequency of carrier transmitted by microwave pilot is in the range of | 
| A. | 1000 kHz to 1500 kHz | 
| B. | 2000 kHz to 5000 kHz | 
| C. | 900 kHz to 6000 kHz | 
| D. | 10000 kHz to 15000 kHz | 
| Answer» D. 10000 kHz to 15000 kHz | |
| 38. | For which of the following protection from negative sequence current is provided? | 
| A. | Generators | 
| B. | Motors | 
| C. | Transmission line | 
| D. | Transformers | 
| Answer» B. Motors | |
| 39. | Impedance relay can be used for | 
| A. | Phase faults only | 
| B. | Earth faults only | 
| C. | Both earth and phase faults | 
| D. | None of the above | 
| Answer» B. Earth faults only | |
| 40. | What is the most important property which makes the SF6 very efficient medium for circuit breaking? | 
| A. | Is non toxic and non inflammable. | 
| B. | Has a high dielectric constant. | 
| C. | Has a high breakdown strength | 
| D. | Is highly electronegative gas | 
| Answer» E. | |
| 41. | Least number of faults are generally reported for | 
| A. | Transmission lines | 
| B. | Cables | 
| C. | Switchgears | 
| D. | Transformers | 
| Answer» C. Switchgears | |
| 42. | The short-circuit in any winding of the transformer is the result of | 
| A. | Mechanical vibration | 
| B. | Insulation failure | 
| C. | Loose connection | 
| D. | Impulse voltage | 
| Answer» E. | |
| 43. | How many relays are used to detect interphase fault of a three line system? | 
| A. | One | 
| B. | Two | 
| C. | Three | 
| D. | Six | 
| Answer» D. Six | |
| 44. | What is the advantage of HRC fuses over Rewirable fuses? | 
| A. | High speed operation | 
| B. | High rupturing capacity | 
| C. | No ageing effect. | 
| D. | All of the above. | 
| Answer» E. | |
| 45. | Rate of rise of restriking voltage depend on_____________? | 
| A. | Type of circuit breaker. | 
| B. | Capacitance of the system. | 
| C. | Inductance of the system. | 
| D. | Both (b) and (c) | 
| Answer» E. | |
| 46. | What is the breaking capacity of the air blast circuit breaker? | 
| A. | 5000 MVA | 
| B. | 6000 MVA | 
| C. | 7000 MVA | 
| D. | 10000 MVA | 
| Answer» D. 10000 MVA | |
| 47. | Minimum working voltage will be least in case of | 
| A. | Silver | 
| B. | Graphite | 
| C. | Carbon | 
| D. | Tungsten | 
| Answer» B. Graphite | |
| 48. | The interrupting time of a circuit breaker is the period between the instant of_________. | 
| A. | Initiation of short circuit and the arc extinction on an opening operation. | 
| B. | Energizing the trip circuit and the arc extension on an opening operation. | 
| C. | Initiation of short circuit and the parting of primary arc contacts. | 
| D. | Energizing of the trip circuit and the parting of primary arc contacts. | 
| Answer» C. Initiation of short circuit and the parting of primary arc contacts. | |
| 49. | For ground fault we prefer | 
| A. | Plain impedance relay | 
| B. | Directional over current relay | 
| C. | Mho relay | 
| D. | Reactance relay | 
| Answer» E. | |
| 50. | Protective relays can be designed to respond to ___________. | 
| A. | Light intensity, impedance | 
| B. | Temperature, resistance, reactance | 
| C. | Voltage and current | 
| D. | All of these | 
| Answer» E. | |