				This section includes 20 Mcqs, each offering curated multiple-choice questions to sharpen your Power Systems knowledge and support exam preparation. Choose a topic below to get started.
| 1. | A blocked electric current of 4000 A is passing through the primary side of a converter having 400/5 A current. The plug setting of the electric current relay is set at 50% at the secondary of the electric current converter. What will be the plug setting multiplier? | 
| A. | 20 | 
| B. | 30 | 
| C. | 10 | 
| D. | 40 | 
| Answer» B. 30 | |
| 2. | For differential protection of power transformer (delta-delta) the current transformers will have | 
| A. | Delta-delta connection | 
| B. | Star-delta connection | 
| C. | Star-star connection | 
| D. | Delta-star connection | 
| Answer» D. Delta-star connection | |
| 3. | Impedance relay is used on______ transmission lines. | 
| A. | Short | 
| B. | Medium | 
| C. | Long | 
| D. | All | 
| Answer» C. Long | |
| 4. | A 11 kV 100 MVA alternator is grounded through a resistance of 4 Ω. The C.T.s have a ratio of 500/5. The relay is set to operate when there is an out of balance current of 2 A. What percentage of generator winding will be protected by the percentage differential protection scheme? | 
| A. | 93.7 | 
| B. | 6.3 | 
| C. | 87.4 | 
| D. | 84.5 | 
| Answer» D. 84.5 | |
| 5. | If for an IDMT relay with a plug setting of 50% and a CT ration of 400/5, the current is 3000 A, then the plug setting multiplier would be: | 
| A. | 7.5 | 
| B. | 15 | 
| C. | 18.75 | 
| D. | 37.5 | 
| Answer» C. 18.75 | |
| 6. | In case of short-tie-line fed at both the ends, for protection | 
| A. | reactance relay is the best choice | 
| B. | ohm relay is the best choice | 
| C. | mho relay is the best choice | 
| D. | Both (1) and (3) | 
| Answer» D. Both (1) and (3) | |
| 7. | Buchholz relay is used on: | 
| A. | Oil cooled transformer | 
| B. | Air cooled transformer | 
| C. | Welding transformer | 
| D. | Furnace transformer | 
| Answer» B. Air cooled transformer | |
| 8. | A 3 – Phase transformer rated for 33 kV/ 11kV is connected in delta/star as shown in figure. The current transformers (CTs) on low land high voltage sides have a ratio of 500/5. Find the current \({i_1}\) and \({i_2}\), of the fault current is 300 A as shown in figure | 
| A. | \({i_1} = \frac{1}{{\sqrt 3 A}},{i_2} = 0A\) | 
| B. | \({i_1} = 0A\), \({i_2} = 0A\) | 
| C. | \({i_1} = 0A,{i_2} = \frac{1}{{\sqrt 3 A}}\) | 
| D. | \({i_1} = \frac{1}{{\sqrt 3 A}},{i_2} = \frac{1}{{\sqrt 3 A}}\) | 
| Answer» B. \({i_1} = 0A\), \({i_2} = 0A\) | |
| 9. | Distance protection relay is used in: | 
| A. | Transformer | 
| B. | Generator | 
| C. | Transmission line | 
| D. | Motor | 
| Answer» D. Motor | |
| 10. | Determine operating current of the relay, for 5 A, 2.2-sec IDMT rating, and 125% relay setting? | 
| A. | 11 A | 
| B. | 4 A | 
| C. | 12.5 A | 
| D. | 6.25 A | 
| Answer» E. | |
| 11. | An electromagnetic attraction type relay operates on ______. | 
| A. | Pulsated DC | 
| B. | AC only | 
| C. | DC only | 
| D. | Both AC & DC | 
| Answer» E. | |
| 12. | In induction type directional over current relay the driving torque is due to interaction of magnetic fields derived from | 
| A. | current in the potential coil | 
| B. | both voltage and current in the relay windings | 
| C. | directional element and non-directional element | 
| D. | non-directional element and the trip circuit | 
| Answer» D. non-directional element and the trip circuit | |
| 13. | Directional overcurrent relay is used for the protection of | 
| A. | long transmission lines | 
| B. | large power transformers | 
| C. | ring main distribution lines | 
| D. | radial distribution lines | 
| Answer» D. radial distribution lines | |
| 14. | If the PSM is 8, the relay setting is 125% and CT ratio is 400 : 1, then the value of fault current will be: | 
| A. | 4550 A | 
| B. | 5000 A | 
| C. | 3000 A | 
| D. | 4000 A | 
| Answer» E. | |
| 15. | In case of transformer Buchholz relay is used to protect from ________. | 
| A. | High voltage surges | 
| B. | Overload faults | 
| C. | Incipient faults | 
| D. | Earth faults | 
| Answer» D. Earth faults | |
| 16. | A distance relay with inherent directional property is known as | 
| A. | Buchholtz relay | 
| B. | Admittance relay | 
| C. | Directional over current relay | 
| D. | Directional switched relay | 
| Answer» C. Directional over current relay | |
| 17. | IDMT full form is: | 
| A. | Inverse Distance maximum Time Relay | 
| B. | Inverse Definite Minimum Time Relay | 
| C. | Inverse Distance Minimum Time Relay | 
| D. | Inverse Definite Maximum Time Relay | 
| Answer» C. Inverse Distance Minimum Time Relay | |
| 18. | A relay is connected to a 400/5 A current transformer and set for 150%. The primary fault current of 2400 A needs a plug setting multiplier of | 
| A. | 2 | 
| B. | 4 | 
| C. | 6 | 
| D. | 8 | 
| Answer» C. 6 | |
| 19. | An earth fault relay has a setting of 150% and a current rating of 5 A. It is connected to a current transformer of ratio 200:5. The current in the primary for which the relay picks up is | 
| A. | 7.5 A | 
| B. | 20 A | 
| C. | 300 A | 
| D. | 1500 A | 
| Answer» D. 1500 A | |
| 20. | A power system with two generators is shown in the figure below. The system (generators, buses and transmission lines) is protected by six overcurrent relays R1 to R6. Assuming a mix of directional and non-directional relays at appropriate locations, the remote backup relays for R4 are | 
| A. | R1, R2 | 
| B. | R2, R6 | 
| C. | R2, R5 | 
| D. | R1, R6 | 
| Answer» E. | |