1. |
A single wattmeter is connected to measure the reactive power of a three-phase, three-wire balanced load. The line current is 17A and the line voltage is 440V. Calculate the power factor of the load if the reading of the wattmeter is 4488 VAR. |
A. | 0.6 |
B. | 0.8 |
C. | 1 |
D. | 1.2 |
Answer» C. 1 | |
2. |
The total reactive power in the load while measuring the reactive power with wattmeter is? |
A. | 3V<sub>L</sub>I<sub>L</sub>cos |
B. | 3V<sub>L</sub>I<sub>L</sub>tan |
C. | 3V<sub>L</sub>I<sub>L</sub>sin |
D. | 3 V<sub>L</sub>I<sub>L</sub>sec |
Answer» D. 3 V<sub>L</sub>I<sub>L</sub>sec | |
3. |
The wattmeter reading while measuring the reactive power with wattmeter is? |
A. | V<sub>L</sub>I<sub>L</sub>sec |
B. | V<sub>L</sub>I<sub>L</sub>sin |
C. | V<sub>L</sub>I<sub>L</sub>tan |
D. | V<sub>L</sub>I<sub>L</sub>cos |
Answer» C. V<sub>L</sub>I<sub>L</sub>tan | |
4. |
The readings of the two watt meters used to measure power in a capacitive load are -3000W and 8000W respectively. Find the power factor. |
A. | 0.25 |
B. | 0.5 |
C. | 0.75 |
D. | 1 |
Answer» B. 0.5 | |
5. |
The readings of the two watt meters used to measure power in a capacitive load are -3000W and 8000W respectively. Calculate the input power. Assume RYB sequence. |
A. | 5 |
B. | 50 |
C. | 500 |
D. | 5000 |
Answer» E. | |
6. |
The input power to a three-phase load is 10kW at 0.8 Pf. Two watt meters are connected to measure the power. Find the reading of lower reading wattmeter. |
A. | 1.835 |
B. | 2.835 |
C. | 3.835 |
D. | 4.835 |
Answer» C. 3.835 | |
7. |
The input power to a three-phase load is 10kW at 0.8 Pf. Two watt meters are connected to measure the power. Find the reading of higher reading wattmeter. |
A. | 7.165 |
B. | 6.165 |
C. | 6.165 |
D. | 4.165 |
Answer» B. 6.165 | |
8. |
The wattmeter method is used to measure power in a three-phase load. The wattmeter readings are 400W and -35W. Find the reactive power. |
A. | 751.44 |
B. | 752.44 |
C. | 753.44 |
D. | 754.44 |
Answer» D. 754.44 | |
9. |
The wattmeter method is used to measure power in a three-phase load. The wattmeter readings are 400W and -35W. Find the power factor. |
A. | 0.43 |
B. | 0.53 |
C. | 0.63 |
D. | 0.73 |
Answer» B. 0.53 | |
10. |
The wattmeter method is used to measure power in a three-phase load. The wattmeter readings are 400W and -35W. Calculate the total active power. |
A. | 360 |
B. | 365 |
C. | 370 |
D. | 375 |
Answer» C. 370 | |