MCQOPTIONS
Saved Bookmarks
This section includes 10 Mcqs, each offering curated multiple-choice questions to sharpen your Power Systems knowledge and support exam preparation. Choose a topic below to get started.
1. |
Suppose the transmission line is loaded with its surge impedance, the receiving-end voltage is greater than sending end voltage. |
A. | True |
B. | False |
Answer» C. | |
2. |
A single phase 50 hz, generator supplies an inductive load of 5 MW at a power factor of 0.8 lagging using OHTL over 20 km. The resistance and reactance are 0.39 and 3.96 . The voltage at receiving station is maintained at 10 KV. The sending end voltage is 11.68 kV. If the voltage regulation is reduced to 50%, then the receiving end current at this operation mode will be _____________ |
A. | 526 A |
B. | 549 A |
C. | 521 A |
D. | 580 A |
Answer» B. 549 A | |
3. |
A single phase 50 hz, generator supplies an inductive load of 5 MW at a power factor of 0.8 lagging using OHTL over 20 km. The resistance and reactance are 0.39 and 3.96 . The voltage at receiving station is maintained at 10 KV. The sending end voltage is 11.68 kV. If the voltage regulation is reduced to 50%, then the power factor angle at this operation mode will be ________ |
A. | 18.04 , lagging |
B. | 18.04 , leading |
C. | 21.06 , leading |
D. | 21.06 , lagging |
Answer» B. 18.04 , leading | |
4. |
A single phase 50 hz, generator supplies an inductive load of 5 MW at a power factor of 0.8 lagging using OHTL over 20 km. The resistance and reactance are 0.39 and 3.96 . The voltage at receiving station is maintained at 10 KV. The sending end voltage is 11.68 kV. If the voltage regulation is reduced to 50%, then the power factor at this operation mode will be ____________ |
A. | 0.95, lagging |
B. | 0.92, leading |
C. | 0.95, lagging |
D. | 0.90, leading |
Answer» B. 0.92, leading | |
5. |
A single phase 50 hz, generator supplies an inductive load of 5 MW at a power factor of 0.8 lagging using OHTL over 20 km. The resistance and reactance are 0.39 and 3.96 . The voltage at receiving station is maintained at 10 KV. The sending end voltage is 11.68 kV. If the voltage regulation is reduced to 50%, then the power factor angle at this operation mode will be _____________ |
A. | 18.04 |
B. | 8.04 |
C. | 21.06 |
D. | 12 |
Answer» B. 8.04 | |
6. |
A single phase 50 hz, generator supplies an inductive load of 5 MW at a power factor of 0.8 lagging using OHTL over 20 km. The resistance and reactance are 0.39 and 3.96 . The voltage at receiving station is maintained at 10 KV. The sending end voltage is 11.68 kV. If the voltage regulation is reduced to 50%, then the power factor at this operation mode will be _________________ |
A. | 0.95 |
B. | 0.92 |
C. | 0.74 |
D. | 0.90 |
Answer» B. 0.92 | |
7. |
A single phase 50 hz, generator supplies an inductive load of 5 MW at a power factor of 0.8 lagging using OHTL over 20 km. The resistance and reactance are 0.39 and 3.96 . The voltage at receiving station is maintained at 10 KV. The sending end voltage is 11.68 kV. The new sending end voltage at the half the voltage regulation is _____________ |
A. | 10.84 kV |
B. | 11.84 kV |
C. | 8.84 kV |
D. | 16.2 kV |
Answer» B. 11.84 kV | |
8. |
A single phase 50 hz, generator supplies an inductive load of 5 MW at a power factor of 0.8 lagging using OHTL over 20 km. The resistance and reactance are 0.39 and 3.96 . The voltage at receiving station is maintained at 10 KV. The sending end voltage is 11.68 kV. The half the voltage regulation will be _____________ |
A. | 8.4 % |
B. | 16.8 % |
C. | 14.2% |
D. | 10.5% |
Answer» B. 16.8 % | |
9. |
A single phase 50 hz, generator supplies an inductive load of 5 MW at a power factor of 0.8 lagging using OHTL over 20 km. The resistance and reactance are 0.39 and 3.96 . The voltage at receiving station is maintained at 10 KV. Identify the transmission line and the voltage regulation. |
A. | STL, 11.68% |
B. | MTL, 11.68 |
C. | STL, 21.5% |
D. | MTL, 14.2% |
Answer» B. MTL, 11.68 | |
10. |
A single phase 50 hz, generator supplies an inductive load of 5 MW at a power factor of 0.8 lagging using OHTL over 20 km. The resistance and reactance are 0.39 and 3.96 . The voltage at receiving station is maintained at 10 KV. The sending end voltage is 11.68 kV. The voltage regulation will be _______ |
A. | 16.8 % |
B. | 18.8% |
C. | 21.75% |
D. | 12.8% |
Answer» B. 18.8% | |