1.

A single phase 50 hz, generator supplies an inductive load of 5 MW at a power factor of 0.8 lagging using OHTL over 20 km. The resistance and reactance are 0.39 and 3.96 . The voltage at receiving station is maintained at 10 KV. The sending end voltage is 11.68 kV. If the voltage regulation is reduced to 50%, then the power factor at this operation mode will be _________________

A. 0.95
B. 0.92
C. 0.74
D. 0.90
Answer» B. 0.92


Discussion

No Comment Found

Related MCQs