Explore topic-wise MCQs in Power Systems.

This section includes 7 Mcqs, each offering curated multiple-choice questions to sharpen your Power Systems knowledge and support exam preparation. Choose a topic below to get started.

1.

Over the length of one transposition cycle of a power line, the total flux linkages of a nearby telephone line are zero for the balanced three phase currents.

A. The above statement is valid
B. The above statement is invalid
C. It can t be concluded
D. The above statement is valid for all conditions.
Answer» B. The above statement is invalid
2.

Over the length of one transposition cycle of a power line, the total flux linkages of a nearby telephone line are zero for the unbalanced three phase currents.

A. True
B. False
Answer» C.
3.

6.Transposition is the mean to balance ____________

A. Inductance
B. Voltage
C. Current
D. All of the mentioned
Answer» B. Voltage
4.

(I) Unsymmetrical spacing configurations cause the line interference.
(II) Unsymmetrical spacing causes the voltage induction in the communication lines.

A. (I) and (II) are valid
B. Only (I) is valid
C. Only (II) is valid
D. Both are invalid
Answer» B. Only (I) is valid
5.

A 10 MVA, 11 kV alternator has positive, negative and zero sequence reactance of 25%, 40%, 10% respectively. The resistance that must be placed in the neutral such that fault current for a single phase to ground fault will not exceed the rated line current in ohms is __________

A. 11.7
B. 12.8
C. 2.66
D. 5.2
Answer» B. 12.8
6.

A 10 MVA, 11 kV alternator has positive, negative and zero sequence reactance of 25%, 40%, 10% respectively. The resistance that must be placed in the neutral such that fault current for a single phase to ground fault will not exceed the rated line current in pu is _____________

A. 0.97
B. 0.22
C. 0.87
D. 0.45
Answer» B. 0.22
7.

A 10 MVA, 11 kV alternators has positive, negative and zero sequence reactance of 25%, 40%, 10% respectively. The resistance that must be placed in the neutral such that zero sequence of fault current for a single phase to ground fault will not exceed the rated line current in pu is ______

A. 0.22
B. 0.11
C. 0.16
D. 0.97
Answer» B. 0.11