1. |
Over the length of one transposition cycle of a power line, the total flux linkages of a nearby telephone line are zero for the balanced three phase currents. |
A. | The above statement is valid |
B. | The above statement is invalid |
C. | It can t be concluded |
D. | The above statement is valid for all conditions. |
Answer» B. The above statement is invalid | |
2. |
Over the length of one transposition cycle of a power line, the total flux linkages of a nearby telephone line are zero for the unbalanced three phase currents. |
A. | True |
B. | False |
Answer» C. | |
3. |
6.Transposition is the mean to balance ____________ |
A. | Inductance |
B. | Voltage |
C. | Current |
D. | All of the mentioned |
Answer» B. Voltage | |
4. |
(I) Unsymmetrical spacing configurations cause the line interference.
|
A. | (I) and (II) are valid |
B. | Only (I) is valid |
C. | Only (II) is valid |
D. | Both are invalid |
Answer» B. Only (I) is valid | |
5. |
A 10 MVA, 11 kV alternator has positive, negative and zero sequence reactance of 25%, 40%, 10% respectively. The resistance that must be placed in the neutral such that fault current for a single phase to ground fault will not exceed the rated line current in ohms is __________ |
A. | 11.7 |
B. | 12.8 |
C. | 2.66 |
D. | 5.2 |
Answer» B. 12.8 | |
6. |
A 10 MVA, 11 kV alternator has positive, negative and zero sequence reactance of 25%, 40%, 10% respectively. The resistance that must be placed in the neutral such that fault current for a single phase to ground fault will not exceed the rated line current in pu is _____________ |
A. | 0.97 |
B. | 0.22 |
C. | 0.87 |
D. | 0.45 |
Answer» B. 0.22 | |
7. |
A 10 MVA, 11 kV alternators has positive, negative and zero sequence reactance of 25%, 40%, 10% respectively. The resistance that must be placed in the neutral such that zero sequence of fault current for a single phase to ground fault will not exceed the rated line current in pu is ______ |
A. | 0.22 |
B. | 0.11 |
C. | 0.16 |
D. | 0.97 |
Answer» B. 0.11 | |