1.

A 10 MVA, 11 kV alternator has positive, negative and zero sequence reactance of 25%, 40%, 10% respectively. The resistance that must be placed in the neutral such that fault current for a single phase to ground fault will not exceed the rated line current in pu is _____________

A. 0.97
B. 0.22
C. 0.87
D. 0.45
Answer» B. 0.22