1.

The CT supplies current to the current coil of a wattmeter power factor meter, energy meter and, an ammeter. These are connected as?

A. All coils in parallel
B. All coils in series
C. Series-parallel connection with two in each arm
D. Series-parallel connection with one in each arm
Answer» C. Series-parallel connection with two in each arm
2.

Usually a CT has ____________

A. Power overload capacity than PT
B. The same overload capacity as a PT
C. A higher overload capacity than a PT
D. No overload capacity
Answer» D. No overload capacity
3.

The observation when the secondary winding of a current transformer is open-circuited is?

A. The whole of the primary current produces a large value of flux in the core thereby producing a large voltage in the secondary winding
B. The large voltage may act as a safety hazard for the operators and many even raptures the insulation
C. When the large magnetizing force is taken off, it leaves a large value of residual magnetism
D. When the large magnetizing force is taken off, it leaves a small value of residual magnetism
Answer» C. When the large magnetizing force is taken off, it leaves a large value of residual magnetism
4.

A (350 A/ 7A), 50 Hz current transformer has a primary bar. The secondary burden is a pure resistance of 1 and it draws a current of 5 A. The magnetic core requires 350 AT for magnetization. Find the percentage ratio error.

A. 10.56
B. -28.57
C. 11.80
D. -11.80
Answer» C. 11.80
5.

A 200/1 Current Transformer (CT) is wound with 400 turns on the secondary on a toroidal core. When it carries a current of 180 A on the primary, the ratio is found to be -0.5%. If the number of secondary turns is reduced by 1, the new ratio error (in %) will be?

A. 0.0
B. -0.5
C. -1.0
D. -2.0
Answer» D. -2.0
6.

A 1000/5 A, 50 Hz correct transformer has a secondary burden comprising a non-inductance of 2 . What is the ratio error, if the iron loss is 3 W and magnetizing mmf is 250 A?

A. 4%
B. 5.7%
C. 3.6%
D. 4.8%
Answer» C. 3.6%
7.

A 1000/5 A, 50 Hz correct transformer has a secondary burden comprising a non-inductance of 1.6 . The flux in the core at full load is?

A. 160 Wb
B. 180 Wb
C. 200 Wb
D. 150 Wb
Answer» C. 200 Wb
8.

A 50 Hz, bar primary CT has a secondary with 500 turns. The secondary supplies 5 A current into a purely resistive burden of 1 . The magnetizing ampere-turns are 200. What is the ratio error at full load, if the iron loss is 1.5 W and magnetizing mmf is 100 A?

A. Zero
B. 45 Wb
C. 25.5 Wb
D. 100 Wb
Answer» C. 25.5 Wb
9.

A 50 Hz, bar primary CT has a secondary with 800 turns. The secondary supplies 7 A current into a purely resistive burden of 2 . The magnetizing ampere-turns are 300. The phase angle is?

A. 3.1
B. 85.4
C. 94.6
D. 175.4
Answer» B. 85.4