The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults? |
| A. | 76.4 |
| B. | 23.6 |
| C. | 73 |
| D. | None of the mentioned |
| Answer» C. 73 | |