

MCQOPTIONS
Saved Bookmarks
1. |
Exhaust gases (c P = 1.12 k J/kg K) flowing through a tubular heat exchanger at the rate of 1200 kg/hr are cooled from 400 degree Celsius to 120 degree Celsius. This cooling is affected by water (c P = 4.18 k J/kg K) that enters the system at 10 degree Celsius at the rate of 1500 kg/hr. If the overall heat transfer coefficient is 500 k J/m2 hr degree, what heat exchanger area is required to handle the load for counter flow arrangement? |
A. | 2.758 m<sup>2</sup> |
B. | 3.758 m<sup>2</sup> |
C. | 4.758 m<sup>2</sup> |
D. | 5.758 m<sup>2</sup> |
Answer» C. 4.758 m<sup>2</sup> | |