During an air-conditioning of a plant, the room sensible heat load is 40 kW and room latent heat load is 10 kW, ventilation air is 25% of supply air. At full load, the room sensible heat factor will be |
| A. | 0.9 |
| B. | 0.8 |
| C. | 0.7 |
| D. | 0.6 |
| Answer» C. 0.7 | |