1. |
A single - phase 50 kVA, 250V/ 500 V two winding transformer has an efficiency of 95% at full load, unity power factor. If it is reconfigured as a 500 V/ 750 V auto-transformer, its efficiency at its new rated load at unity power factor will be |
A. | 95.752% |
B. | 97.851% |
C. | 98.276% |
D. | 99.241% |
Answer» D. 99.241% | |