MCQOPTIONS
Saved Bookmarks
| 1. |
A single phase 50 hz, generator supplies an inductive load of 5 MW at a power factor of 0.8 lagging using OHTL over 20 km. The resistance and reactance are 0.39 and 3.96 . The voltage at receiving station is maintained at 10 KV. The sending end voltage is 11.68 kV. The voltage regulation will be _______ |
| A. | 16.8 % |
| B. | 18.8% |
| C. | 21.75% |
| D. | 12.8% |
| Answer» B. 18.8% | |