1.

A city is to install rapid sand filters downstream of the clarifiers. The design loading rate is selected to be 160 m3/ (m2.d). The design capacity of the water works is 0.35 m3/s. The maximum surface per filter is limited to 50 m2 and find out the normal filtration rate?

A. 154.3 m<sup>3</sup>/(m<sup>2</sup>.d)
B. 154.6 m<sup>3</sup>/(m<sup>2</sup>.d)
C. 155.6 m<sup>3</sup>/(m<sup>2</sup>.d)
D. 155.3 m<sup>3</sup>/(m<sup>2</sup>.d)
Answer» B. 154.6 m<sup>3</sup>/(m<sup>2</sup>.d)