A 50 Hz alternator is rated 500 MVA, 20 kV, with Xd = 1.0 per unit and X"d = 0.2 per unit. It supplies a purely resistive load of 400 MW at 20 kV. The load is connected directly across the generator terminals when a symmetrical fault occurs at the load terminals. The initial rms current in the generator in per unit is __________

A. 3.022
B. 3.22
C. 53.26
D. 542.5
Answer» C. 53.26