A 230 V (phase), 50 Hz, three - phase, 4 wire system has a phase sequence ABC. A unity power - factor load of 4 kW is connected between phase A and neutral N. It is desired to achieve zero neutral current through the use of a pure inductor and a pure capacitor in the other two phase. The value of inductor and capacitor is |
A. | 72.95 mH in phase C and 139.02 F in phase B |
B. | 72.95 mH in phase B and 139.02 F in phase C |
C. | 42.12 mH in phase C and 240.79 F in phase B |
D. | 42.12 mH in phase B and 240.79 F in phase C |
Answer» C. 42.12 mH in phase C and 240.79 F in phase B | |