A 100 MVA, 50 Hz turbo-generator operates at no load at 3000 rpm. A load of 25 MW is suddenly applied to the machine and the steam valve to the turbine commences to open after 0.6 seconds due to the governor time-lag. Assuming the inertia constant H = 5.0 kW-s per kVA of the generator rating, the frequency to which the generated voltage drops before the steam-flow commences to meet the new load is

A. 49. Hz
B. 50.15 Hz
C. 49.24 Hz
D. 49.82 Hz
Answer» D. 49.82 Hz