A 10 MVA, 11 kV alternators has positive, negative and zero sequence reactance of 25%, 40%, 10% respectively. The resistance that must be placed in the neutral such that zero sequence of fault current for a single phase to ground fault will not exceed the rated line current in pu is ______ |
| A. | 0.22 |
| B. | 0.11 |
| C. | 0.16 |
| D. | 0.97 |
| Answer» B. 0.11 | |