A 10 MVA, 11 kV alternator has positive, negative and zero sequence reactance of 25%, 40%,10% respectively. The resistance that must be placed in the neutral such that zero sequence of fault current for a single phase to ground fault will not exceed the rated line current in ohms is |
| A. | 2.66 |
| B. | 1.66 |
| C. | 12.1 |
| D. | 0.22 |
| Answer» B. 1.66 | |