50 Hz generator is delivering 50% of the power that is capable of delivering through a transmission line to an infinite bus. A fault occurs that increases the reactance between the generator and bus to 500% before the fault. When the fault is isolated, the maximum power that can be delivered is 75% of the original maximum value. The critical clearing angle for the condition is desired, will be

A. 67.44
B. 70
C. 50.4
D. none of these
Answer» B. 70