1.

An ability of Relay system to operate under predetermined condition is called ________.

A. Sensitivity
B. Selectivity
C. Stability
D. Reliability
Answer» B. Selectivity
2.

Over speed protection of a generator is done by

A. Governor
B. Differential protection
C. Over current relay
D. Alarm
Answer» B. Differential protection
3.

In a 3-step distance protection, the reach of the three zones of the relay at the beginning of the first line typically extends into

A. 100% of the first line, 50% of the second line and 20% of the third line
B. 80% of the first line, 50% of the second line and 20% of the third line
C. 80% of the first line, 50% of the second line and 10% of the third line
D. 50% of the first line, 50% of the second line and 20% of the third line
Answer» C. 80% of the first line, 50% of the second line and 10% of the third line
4.

A good fuse wire must have:

A. High melting point
B. High Ohmic losses
C. High Conductivity
D. High Deterioration
Answer» D. High Deterioration
5.

Material used for making small rating fuses is

A. aluminum
B. copper
C. silver
D. lead and tin
Answer» E.
6.

During current chopping the current actually breaks...

A. During the instant of natural current zero
B. Before the instant of natural current zero
C. After the instant of natural current zero
D. Irrespective of the instant of natural zero
Answer» C. After the instant of natural current zero
7.

Earth breaker circuit uses

A. Polarized Relay
B. Reed Relay
C. Latching Relay
D. Machine Tool Relay
Answer» D. Machine Tool Relay
8.

Directional relays are based on the flow of

A. Power
B. Voltage wave
C. Current
D. Field
Answer» B. Voltage wave
9.

A sample power system network is shown in the figure given below. The reactance marked are in P.U. What is the P.U. value of Y22 of Bus Admittance matrix (YBus)?

A. j10.0
B. j0.4
C. –j0.1
D. –j20.0
Answer» E.
10.

In digital relay, the ON and OFF state is represented in binary numbers as _____ and _____ respectively.

A. 0, 1
B. 1, 0
C. 0, 0
D. 1, 1
Answer» C. 0, 0
11.

Determine the time of operation of a relay of rating 5 A, 2.2s IDMT and having a relay setting of 125%, TMS = 0.6. It is connected to the supply circuit through a CT 400 : 5 ratio. The fault current is 4000 A.PSM25810Time1083.22.5

A. 1.89 s
B. 1.87 s
C. 1.93 s
D. 1.92 s
Answer» E.
12.

For rural electrification in India, which circuit breaker is generally used?

A. Oil
B. SF6
C. Vacuum
D. Air blast
Answer» D. Air blast
13.

Consider the following statements:HRC fuse as compared to rewirable fuse has:(A) no aging effect(B) high speed of operation(C) high rupturing capacity

A. Only A and B
B. Only B
C. Only B and C
D. All three
Answer» E.
14.

Inverted operation of a generator can be protected using ______.

A. Over frequency relay
B. Over speed relay
C. Reverse power relay
D. Overload relay
Answer» D. Overload relay
15.

Over conventional electromechanical relays, the static relays have the advantages of

A. low power consumption, less maintenance and greater sensitivity
B. compact size and quick operation
C. wide range of characteristics approaching more or less to ideal requirement
D. All of the above
Answer» E.
16.

A 10 kV alternator is protected by the balanced circulating current system. It is grounded through a 10 Ω resistance. The protective relay operates at 1.8 A in the pilot wires, which are connected to the secondary windings of 1000/5 CT. The percentage winding which remains unprotected will be

A. 20%
B. 31%
C. 62%
D. 76%
Answer» D. 76%
17.

In transformers, Buchholz relay is used for detecting:

A. internal faults
B. external faults
C. insulation failure
D. overcurrent
Answer» B. external faults
18.

For earth fault, the preferred relay is

A. overcurrent relay
B. impedance relay
C. directional relay
D. reactance relay
Answer» E.
19.

________ is not a method of high resistance interruption of arc extinction:

A. Blast effect
B. Arc lengthening
C. Arc constraining
D. Arc cooling
Answer» B. Arc lengthening
20.

Magnitude relay is also called _____ .

A. Thermal Relay
B. Hybrid Relay
C. Induction Relay
D. Reed Relay
Answer» D. Reed Relay
21.

Plug setting of an electromagnetic relay can be altered by varying

A. Number of ampere turns
B. Air gap of magnetic path
C. Adjustable back stop
D. None of these
Answer» B. Air gap of magnetic path
22.

For the protection of a very long extra high voltage line, the protective relay used is:

A. Over current with extremely inverse characteristics
B. Percentage differential relay
C. Reactance type distance relay
D. Mho type distance relay
Answer» E.
23.

Buchholz relay is used to protect

A. Transmission line
B. Generator
C. Transformer
D. Motor
Answer» D. Motor
24.

Induction relays are used with:

A. d.c. quantities
B. a.c. quantities
C. d.c. and a.c. both
D. None of these
Answer» C. d.c. and a.c. both
25.

ELCB is a

A. Safety device
B. Current controlling device
C. Voltage controlling device
D. Both 2 and 3
Answer» B. Current controlling device
26.

Power stations and sub-stations are protected against direct strokes of lightning using:

A. Rod gap arrester
B. Overhead ground wires
C. Earthing screen
D. Horn gap arrester
Answer» D. Horn gap arrester
27.

Programmable Logical Controllers are the devices that were invented basically to replace

A. Switches
B. Circuit Breakers
C. Relays
D. None of the above
Answer» D. None of the above
28.

An over current relay of current rating 5 A and setting 150% is connected to the secondary of CT of ratio 300:5. Then the current in the lines for which the relay pick up is

A. 300 A
B. 450 A
C. 150 A
D. 200 A
Answer» C. 150 A
29.

Earthing is necessary to give protection against

A. Danger of electric shock
B. Voltage fluctuation
C. Overloading
D. High temperature of conductor
Answer» B. Voltage fluctuation
30.

A fuse is never inserted in:

A. Neutral wire
B. Negative of DC circuit
C. Positive of DC circuit
D. Phase line
Answer» B. Negative of DC circuit
31.

In circuit breaker, to facilitate arc quenching, dielectric strength can be increased by

A. Lengthening of the gap
B. Cooling
C. Blast effect
D. All of these
Answer» E.
32.

A Buchholz relay is used for

A. protection of transformer against all internal faults.
B. protection of transformer against all external faults.
C. protection of transformer against both internal and external faults.
D. protection of induction motors
Answer» B. protection of transformer against all external faults.
33.

Making capacity of a circuit breaker is equal to

A. 2.55 times symmetrical breaking capacity
B. 1.5 times symmetrical breaking capacity
C. √2 times symmetrical breaking capacity
D. Symmetrical breaking capacity
Answer» B. 1.5 times symmetrical breaking capacity
34.

Buccholz relay is essential for protection against transformer’s ______.

A. inner-turn fault
B. HT and LT fault
C. earth-fault
D. series fault
Answer» B. HT and LT fault
35.

In thyrite lightning arrester, on doubling the voltage the current increases to ______.

A. 4 times
B. 12.6 times
C. 2 times
D. 6.6 times
Answer» C. 2 times
36.

Phase modifier is normally installed in the case of

A. short transmission lines
B. medium length lines
C. long length lines
D. all length lines
Answer» D. all length lines
37.

A reactance relay is also known as:

A. Directional restrained overcurrent relay
B. Directional restrained directional relay
C. Voltage restrained directional relay
D. Voltage restrained overcurrent relay
Answer» B. Directional restrained directional relay
38.

Earthing transformer is used to

A. Improve neutral wire’s current capacity
B. Avoid overheating of transformer
C. Provide artificial earthing
D. Avoid harmonics
Answer» D. Avoid harmonics
39.

Lightning arrestor is consists of:

A. A spark gap in parallel with non-linear resistor
B. A spark gap in parallel with linear resistor
C. A spark gap in series with non-linear resistor
D. A spark gap in series with linear resistor
Answer» D. A spark gap in series with linear resistor
40.

In busbar protection, what is the method of providing an earthed metal barrier surrounding a bus bar throughout its length called?

A. Distance protection
B. Time graded over current protection
C. Fault bus protection
D. Differential protection
Answer» D. Differential protection
41.

Back up protection is generally employed for protection against:

A. Open circuit faults
B. Earth fault
C. Short circuit fault
D. All of these
Answer» E.
42.

In Rod Gap Arrester, a current limiting resistance is connected in series with the rod in order to ______.

A. Increase the rod gap
B. Avoid cascading of steep fronted waves
C. Avoid continued sparking even at low voltage
D. Reduce breakdown voltage
Answer» D. Reduce breakdown voltage
43.

In oil and air blast circuit breakers, the current zero interruption is attained by

A. Increase the length of the contact gap
B. cooling and blast effect
C. deionizing the oil with forced air
D. both (a) and (b)
Answer» E.
44.

In the case of circuit breakers if the length of arc increases, its resistance:

A. decreases
B. increases
C. remain same
D. sometimes increases or decreases
Answer» C. remain same
45.

A 3-phase transformer rated for 33/6.6 kV is connected to a star/delta and the current transfer on the LV side has a ratio of 500 : 5. Determine the ratio of the current transformer on the HV side.

A. 100 : 5
B. \(110:\frac{5}{{\sqrt 3 }}\)
C. \(100:\frac{5}{{\sqrt 3 }}\)
D. 110 : 5
Answer» D. 110 : 5
46.

A merz-price protection is suitable for

A. Transformers
B. Alternators
C. Feeders
D. Transmission lines
Answer» C. Feeders
47.

Overspeed protection of the alternator is done with the help of

A. Over current relay
B. Alarm
C. Governor
D. Differential relay
Answer» D. Differential relay
48.

If the time of operation of a relay for unity TMS is 10 secs, the time of operation for 0.5 TMS will be:

A. 20 secs
B. 5 secs
C. 10 secs
D. 15 secs
Answer» C. 10 secs
49.

A Mho relay is a:

A. Voltage restrained directional relay
B. Voltage controlled over-current relay
C. Directional restrained over-current relay
D. Directional restrained over-voltage relay
Answer» B. Voltage controlled over-current relay
50.

A thyrite lightning arrester has

A. Inverse resistance characteristics
B. a gap
C. efficient earthing
D. a combination of inverse resistance characteristics and gap
Answer» E.