| 1. |
A 600-kVA, single-phase transformer with 0.012 pu resistance and 0.06 pu reactance is connected in parallel with a 300-kVA transformer with 0.014 pu resistance and 0.045 pu reactance to share a load of 800 kVA at 0.8 pf lagging. Find how they share the load (a) when both the secondary voltages are 440 V. |
| A. | S<sub>1</sub>= 377+j305.2 |
| B. | S<sub>2</sub>= 377-j305.2 |
| C. | S<sub>1</sub>= 264+ j171.6 |
| D. | S<sub>1</sub>= 377-j305.2 |
| Answer» E. | |
| 2. |
Which is the correct formula of current flowing through one of the transformers having unequal ratios? |
| A. | I<sub>2</sub>= E<sub>2</sub>Z<sub>1</sub>-(E<sub>1</sub>-E<sub>2</sub>) Z<sub>L</sub> / (Z<sub>1</sub>Z<sub>2</sub> + ZL(Z<sub>1</sub>+Z<sub>2</sub>)) |
| B. | I<sub>1</sub>= E<sub>2</sub>Z<sub>1</sub>+(E<sub>1</sub>+E<sub>2</sub>) Z<sub>L</sub> / (Z<sub>1</sub>Z<sub>2</sub> + ZL(Z<sub>1</sub>+Z<sub>2</sub>)) |
| C. | I<sub>1</sub>= E<sub>2</sub>Z<sub>1</sub>-(E<sub>1</sub>-E<sub>2</sub>) Z<sub>L</sub> / (Z<sub>1</sub>Z<sub>2</sub> ZL(Z<sub>1</sub>-Z<sub>2</sub>)) |
| D. | I<sub>2</sub>= E<sub>2</sub>Z<sub>1</sub>+(E<sub>1</sub>-E<sub>2</sub>) Z<sub>L</sub> / (Z<sub>1</sub>Z<sub>2</sub> + ZL(Z<sub>1</sub>+Z<sub>2</sub>)) |
| Answer» B. I<sub>1</sub>= E<sub>2</sub>Z<sub>1</sub>+(E<sub>1</sub>+E<sub>2</sub>) Z<sub>L</sub> / (Z<sub>1</sub>Z<sub>2</sub> + ZL(Z<sub>1</sub>+Z<sub>2</sub>)) | |
| 3. |
Maximum load kVA is _____________________ |
| A. | greater than addition of individual rated kVAs |
| B. | lesser than addition of individual rated kVAs |
| C. | equal to addition of individual rated kVAs |
| D. | depends on the loading condition |
| Answer» C. equal to addition of individual rated kVAs | |
| 4. |
Which is the correct formula for current flowing through the transformer 1, when they re having equal voltage ratio? |
| A. | I<sub>1</sub>= Z<sub>2</sub>/(Z<sub>1</sub>+Z<sub>2</sub>) *I<sub>L</sub> |
| B. | I<sub>2</sub>= Z<sub>2</sub>/(Z<sub>1</sub>+Z<sub>2</sub>) *I<sub>L</sub> |
| C. | I<sub>1</sub>= Z<sub>1</sub>/(Z<sub>1</sub>+Z<sub>2</sub>) *I<sub>L</sub> |
| D. | I<sub>1</sub>= Z<sub>2</sub>/(Z<sub>1</sub>-Z<sub>2</sub>) *I<sub>L</sub> |
| Answer» B. I<sub>2</sub>= Z<sub>2</sub>/(Z<sub>1</sub>+Z<sub>2</sub>) *I<sub>L</sub> | |
| 5. |
If two transformers secondaries are connected to each other with unequal primary voltage ratio then, __________ |
| A. | no circulating current will flow |
| B. | very high short circuit current will flow |
| C. | small circulating current will flow |
| D. | insufficient information |
| Answer» D. insufficient information | |
| 6. |
If the primary voltages at two transformers V1 and V2 are not equal then on load, we ll get ____________ |
| A. | V<sub>1</sub>-V<sub>2</sub> at secondary |
| B. | E<sub>1</sub>-E<sub>2</sub> at secondary |
| C. | V<sub>1</sub>+V<sub>2</sub> at secondary |
| D. | E<sub>1</sub>+E<sub>2</sub> at secondary |
| Answer» C. V<sub>1</sub>+V<sub>2</sub> at secondary | |