151. |
A 10 kVA 500/100 V transformer has the resistance referred to primary is 0.3 Ω. The equivalent resistance of transformer referred to secondary is: |
A. | 0.10 Ω |
B. | 7.5 Ω |
C. | 0.012 Ω |
D. | 0.21 Ω |
Answer» D. 0.21 Ω | |
152. |
Find primary turns of a 444 V/222 V, 50 Hz single-phase transformer with a core cross-sectional area of 100 cm2, and a maximum flux density of 1.0 T? |
A. | 100 |
B. | 200 |
C. | 222 |
D. | 400 |
Answer» C. 222 | |
153. |
In a transformer, _________ losses are reduced by decreasing the thickness of lamination of magnetic core and yoke. |
A. | copper |
B. | eddy current |
C. | hysteresis |
D. | air friction |
Answer» C. hysteresis | |
154. |
Breather is provided in a transformer to |
A. | absorb moisture of air during breathing |
B. | provide cold air in transformer |
C. | absorb moisture from air entering in transformer |
D. | filter the transformer oil |
Answer» D. filter the transformer oil | |
155. |
A 4 kVA transformer has iron-loss of 200 W and full load copper loss of 200 W. The maximum efficiency at unity power factor will be |
A. | 90.9% |
B. | 85.6% |
C. | 80.6% |
D. | 70.9% |
Answer» B. 85.6% | |
156. |
A dc voltage supply provides 60 V when the output is unloaded. When connected to a load, the output voltage drops to 56 V. The value of the voltage regulation is |
A. | 3.7% |
B. | 5.7% |
C. | 7.1% |
D. | 9.1% |
Answer» D. 9.1% | |
157. |
Power loss in a transformer is known as the _____. |
A. | Difference of current between the secondary and the primary coils. |
B. | Addition of power in the secondary and the primary coils. |
C. | difference of voltage between the secondary and the primary coils. |
D. | Difference of power between the primary and the secondary coils |
Answer» E. | |
158. |
Directions: It consists of two statements, one labeled as the ‘Statement (I)’ and the other as ‘Statement (II)’. Examine these two statements carefully and select the answer using the codes given below:Statement (I): The magnetization curve of the actual power transformer is non-linear and its effect is to introduce higher-order harmonics in the magnetizing currentStatement (II): The effect of the harmonic frequencies can be taken care of by modifying the magnitudes of the phasors involved, and the phasor diagram at the fundamental frequency, with the assumption of a linear magnetization, remains unaffected. |
A. | Statement (I) and Statement (II) are individually true and statement (II) is the correct explanation of statement (II) |
B. | Statement (I) and Statement (II) are individually true but statement (II) is not the correct explanation of statement (I) |
C. | Statement (I) is true but statement (II) is false |
D. | Statement (I) is false but statement (II) is true |
Answer» C. Statement (I) is true but statement (II) is false | |
159. |
A single-phase, \(22\;kVA,\;2200\;V/\;220\;V,\;50\;Hz\), distribution transformer is to be connected as an auto-transformer to get an output voltage of \(2420\;V\). Its maximum \(kVA\) rating as an auto-transformer is |
A. | 22 |
B. | 24.2 |
C. | 242 |
D. | 2420 |
Answer» D. 2420 | |
160. |
Distribution transformers are designed to have maximum efficiency nearly at: |
A. | 100% of full load |
B. | 50% of full load |
C. | 25% of full load |
D. | 10% of full load |
Answer» C. 25% of full load | |
161. |
In a Scott-connected transformer the number of primary and teaser turns respectively are ____ |
A. | N, 2N/√3 |
B. | N/2, N |
C. | √3N/2, N |
D. | N, √3N/2 |
Answer» E. | |
162. |
Core lamination in a transformer decreases _______. |
A. | eddy current loss |
B. | hysteresis loss |
C. | copper loss |
D. | leakage reactance |
Answer» B. hysteresis loss | |
163. |
A 100 VA, 120/12 V transformer is to be connected so as to form a step-up transformer. A Primary voltage of 120 V is applied to the transformer. What is the secondary voltage of the transformer? |
A. | 1.2 V |
B. | 12 V |
C. | 120 V |
D. | 132 V |
Answer» E. | |
164. |
A 20 turns iron cored inductor is connected to a 100 V, 50 Hz source. The maximum flux density in the core is 1 wb/m2. The cross-sectional area of the core in the transformer is |
A. | 0.155 m2 |
B. | 0.225 m2 |
C. | 0.022 m2 |
D. | 0.35 m2 |
Answer» D. 0.35 m2 | |
165. |
On the two sides of a star/delta transformer ________ |
A. | the voltage and current are both in phase |
B. | the voltage and current both differ in phase by 30° |
C. | the voltage differ in phase by 30° but currents are in phase |
D. | the current differ in phase by 30° but voltages are in phase |
Answer» C. the voltage differ in phase by 30° but currents are in phase | |
166. |
Hysteresis loss can be minimized by selecting a material for the core that has: |
A. | Low hysteresis coefficient |
B. | Low transmission coefficient |
C. | Unit hysteresis coefficient |
D. | High hysteresis coefficient |
Answer» B. Low transmission coefficient | |
167. |
During the short circuit test on a small transformer, the frequency is increased from 50 Hz to 200 Hz, the copper losses will decrease by a factor of: |
A. | 16 |
B. | 4 |
C. | 1 |
D. | 1/4 |
Answer» B. 4 | |
168. |
A transformer operates most efficiently at 3/4th full load. Its iron loss (Pi) and full load copper loss (Pc) are related as |
A. | \(\frac{{{P_i}}}{{{P_c}}} = \frac{{16}}{9}\) |
B. | \(\frac{{{P_i}}}{{{P_c}}} = \frac{3}{4}\) |
C. | \(\frac{{{P_i}}}{{{P_c}}} = \frac{4}{3}\) |
D. | \(\frac{{{P_i}}}{{{P_c}}} = \frac{9}{{16}}\) |
Answer» E. | |
169. |
A 2000/200 V, 50 Hz single-phase transformer has an exciting current of 0.5 A and a core-loss of 600 W. When H.V side is energized by the rate voltage and frequency, the magnetizing current is |
A. | 0.1 A |
B. | 0.2 A |
C. | 0.3 A |
D. | 0.4 A |
Answer» E. | |
170. |
A 1-ϕ transformer has total iron losses of 2500 W at 50 Hz and 400 V input supply voltage. When the applied voltage is 200 V and supply frequency is 25 Hz, the total iron loss is found to be 850 W. Calculate the eddy current loss at 400 V 50 Hz. (Consider V/f ratio as constant) |
A. | 2000 W |
B. | 1600 W |
C. | 1500 W |
D. | 1000 W |
Answer» C. 1500 W | |
171. |
A saturable core reactor is basically a |
A. | Variable resistor |
B. | Thermal relay |
C. | Step-down transformer |
D. | Variable impedance |
Answer» E. | |
172. |
In a transformer operating at a constant voltage, if the input frequency increases, the core loss: |
A. | Increases |
B. | Decreases |
C. | Remains constant |
D. | Increases as square of the frequency |
Answer» C. Remains constant | |
173. |
A transformer has a core loss of 140 W at 40 Hz, and 99 W at 30 Hz. The hysteresis and eddy-current losses at 50 Hz, respectively, are |
A. | 110 W and 30 W |
B. | 135 W and 30 W |
C. | 110 W and 50 W |
D. | 135 W and 50 W |
Answer» E. | |
174. |
If the pu impedance of a single-phase transformer is 0.01 + j0.05, then its regulation at p.f. of 0.8 lagging will be ______. |
A. | +2.2% |
B. | -3.8% |
C. | +3.8% |
D. | -2.2% |
Answer» D. -2.2% | |
175. |
In a transformer the core loss is 100 Watt at 40 Hz and 72 Watt at 30 Hz, then eddy current and hysteresis losses at 50 Hz respectively are |
A. | 25 Watt and 105 Watt |
B. | 20 Watt and 100 Watt |
C. | 100 Watt and 32 Watt |
D. | 32 Watt and 100 Watt |
Answer» B. 20 Watt and 100 Watt | |
176. |
Calculate the regulation of the transformer in which ohmic loss is 1% of the output and reactance drop is 5% of the voltage when the power factor is 0.8 lag |
A. | 3.8% |
B. | 3.5% |
C. | 1% |
D. | 5% |
Answer» B. 3.5% | |
177. |
An ideal transformer will not transform:I. PowerII. CurrentIII. FrequencyIV. Voltage |
A. | I and II |
B. | I and III |
C. | II and III |
D. | III and IV |
Answer» C. II and III | |
178. |
Highest rating transformers are likely to find application in |
A. | distribution |
B. | generation |
C. | substation |
D. | transmission |
Answer» C. substation | |
179. |
In the equivalent circuit of transformers the magnetizing circuit branch is drawn in parallel to supply voltage because |
A. | transformer has better operational efficiency |
B. | transformer has almost equal iron loss and copper loss |
C. | transformer’s magnetization current and iron loss remains constant with supply voltage |
D. | transformer’s voltage regulation is better |
Answer» D. transformer’s voltage regulation is better | |
180. |
A distribution transformer is usually a: |
A. | star/star transformer |
B. | delta/delta transformer |
C. | star/delta transformer |
D. | delta/star transformer |
Answer» E. | |
181. |
In an open circuit, a converter of 11 KVA 1100/110 V outputs 100 W of power when 110 V is applied to an LV winding with an open HV winding. If 1100 V is applied on HV winding with open LV winding, what will be the power input? |
A. | 10000 W |
B. | 1000 W |
C. | 100 W |
D. | 10 W |
Answer» D. 10 W | |
182. |
A single-phase two winding transformer is designed to operate at 400/200 V, 50 Hz. If the h.v. side is now energized from a 400 V, 40 Hz source, the no-load l.v. side voltage would be |
A. | 300 V |
B. | 250 V |
C. | 200 V |
D. | 150 V |
Answer» D. 150 V | |
183. |
If the percentage impedances of the two transformers working in parallel are different then |
A. | Transformers will be overheated |
B. | Power factors of both the transformers will be same |
C. | Parallel operation will not be possible |
D. | Parallel operation will still be possible |
Answer» E. | |
184. |
In a transformer, if the iron losses and copper losses are 40.5 kW and 50 kW respectively, then at what fraction of load will the efficiency be maximum? |
A. | 0.8 |
B. | 0.57 |
C. | 0.7 |
D. | 0.9 |
Answer» E. | |
185. |
No iron losses means _______ are zero. |
A. | only hysteresis losses |
B. | only copper losses |
C. | hysteresis and eddy current losses |
D. | eddy current and copper losses |
Answer» D. eddy current and copper losses | |
186. |
An open circuit test is performed on 50 Hz transformer, using variable frequency source and keeping V/f ratio constant, to separate its eddy current and hysteresis losses. The variation of core loss/frequency as function of frequency is shown in the figureThe hysteresis and eddy current losses of the transformer at 25 Hz respectively are |
A. | 250 W and 2.5 W |
B. | 250 W and 62.5 W |
C. | 312.5 W and 62.5 W |
D. | 312.5 W and 250 W |
Answer» C. 312.5 W and 62.5 W | |
187. |
A transformer is supplying a unity power factor load. Power factor on primary side will be: |
A. | About 0.95 lag |
B. | unity |
C. | About 0.95 lead |
D. | zero |
Answer» B. unity | |
188. |
In an ideal transformer, which of the following statement is correct? |
A. | no voltage drops in resistance or leakage reactance |
B. | mmf required to maintain main flux is small |
C. | no core loss |
D. | all the above are correct |
Answer» E. | |
189. |
In a power transformer, copper losses occur in: |
A. | bushing |
B. | insulating oil |
C. | core |
D. | windings |
Answer» E. | |
190. |
Auto transformer is used in transmission and distribution. |
A. | When operater is not available |
B. | When iron losses are to be reduced |
C. | When efficiency consideration is ignored |
D. | When transformation ratio is small |
Answer» E. | |
191. |
In a transformer having a turns ratio of 1 : 5 and a resistance of 1000 Ω connected across the secondary terminals, the resistance offered to the current flowing in the primary will be: |
A. | 40 Ω |
B. | 60 Ω |
C. | 20 Ω |
D. | 200 Ω |
Answer» B. 60 Ω | |
192. |
A transformer having a turn ratio 1 : 5 and a resistance of 1000 ohms is connected across the secondary terminals, the resistance to the current flowing in the primary will be: |
A. | 10 ohms |
B. | 20 ohms |
C. | 40 ohms |
D. | 60 ohms |
Answer» D. 60 ohms | |
193. |
Cores of large power transformers are made from which one of the following? |
A. | Hot-rolled steel |
B. | Cold-rolled non-grain oriented steel |
C. | Cold-rolled gain oriented steel |
D. | Ferrite |
Answer» D. Ferrite | |
194. |
If the copper loss of a transformer at half full load is 400 W, then the copper loss corresponding to full load is: |
A. | 1600 W |
B. | 800 W |
C. | 400 W |
D. | 1200 W |
Answer» B. 800 W | |
195. |
A 200 kVA, 3300/240 V, 50 Hz single-phase transformer has 80 turns on the secondary winding. Assuming an ideal transformer, the primary current I1 and secondary current I2 on full load are nearly |
A. | 60.6 A and 833 A |
B. | 72.2 A and 833 A |
C. | 60.6 A and 720 A |
D. | 72.2 A and 720 A |
Answer» B. 72.2 A and 833 A | |
196. |
During short-circuit test of a transformer, core losses are negligible because |
A. | the current on the secondary side is rated current |
B. | the voltage on the secondary side is zero |
C. | the voltage applied on the primary side is low |
D. | full-load current is not supplied to the transformer |
Answer» D. full-load current is not supplied to the transformer | |
197. |
Consider the following statements concerning the utility of mesh-connected tertiary windings in star-star transformers:1. It is used to suppress harmonic voltages2. It is used to allow flow of earth fault current for operation of protective devices3. It facilitates supply of single-phase loads4. It provides low-reactance paths for zero sequence currentsWhich of these statements are correct? |
A. | 1, 2, 3, and 4 |
B. | 1, 2 and 3 only |
C. | 1, 2 and 4 only |
D. | 3 and 4 only |
Answer» B. 1, 2 and 3 only | |
198. |
Distribution transformers have core losses: |
A. | More than full load copper losses |
B. | Equal to full load copper losses |
C. | Less than full load copper losses |
D. | Negligible compared to full load copper losses |
Answer» D. Negligible compared to full load copper losses | |
199. |
A transformer is working at full load with maximum efficiency. Its iron loss is 1000 W. What will be its copper loss at half full load? |
A. | 1000 W |
B. | 250 W |
C. | 500 W |
D. | 2000 W |
Answer» C. 500 W | |
200. |
A 20 kVA, 2000/200 V, single-phase transformer has a leakage impedance of 8%. What voltage applied to the HV side will result in full-load current flow in the LV side, when the LV side is short-circuited? |
A. | 64 V |
B. | 86 V |
C. | 132 V |
D. | 160 V |
Answer» E. | |