1. |
Five alternators, each of which is rated for 10 MVA, 11 KV with 25% reactance, operate in parallel order. What will be the short circuit level in the bus bar? |
A. | 200 MVA |
B. | 50 MVA |
C. | 300 MVA |
D. | 100 MVA |
Answer» B. 50 MVA | |
2. |
For a fault at the terminals of the synchronous generator, the fault current is maximum for a |
A. | Three phase fault |
B. | Three phase to ground fault |
C. | Line to ground fault |
D. | Line to line fault |
Answer» D. Line to line fault | |
3. |
A 50 Hz, 4 Pole, 500 MVA, 22 kV turbo generator is delivering rated MVA at a power factor of 0.8. Suddenly a fault occurs reducing the electric power output by 40%. Neglect the losses and assume constant power input to the shaft. The accelerating torque in the generator at the time of fault is |
A. | 1.528 MNm |
B. | 1.018 MNm |
C. | 0.848 MNm |
D. | 0.509 MNm |
Answer» C. 0.848 MNm | |
4. |
A lossless transmission line with 0.2 pu reactance per phase uniformly distributed along the length of the line, connecting a generator bus to a load bus, is protected up to 80 % of its length by a distance relay placed at the generator bus. The generator terminal voltage is 1 pu. There is no generation at the load bus. The threshold pu current for operation of the distance relay for a solid three phase-to-ground fault on the transmission line is closest to: |
A. | 1 |
B. | 3.61 |
C. | 5 |
D. | 6.25 |
Answer» E. | |
5. |
Line-to-ground fault occurs: |
A. | Due to short circuit between two conductors |
B. | Due to insulation breakdown between one of the phase and earth |
C. | Due to the breakdown of insulation between two phases and simultaneous breakdown of insulation between the third phase and earth |
D. | Due to fault breakdowns of insulation between two phases and earth occur |
Answer» C. Due to the breakdown of insulation between two phases and simultaneous breakdown of insulation between the third phase and earth | |
6. |
In case of single line to ground fault |
A. | All sequence networks are connected in parallel |
B. | All sequence networks are connected in series |
C. | Positive and negative sequence networks are connected in parallel |
D. | Zero and negative sequence networks are connected in series |
Answer» C. Positive and negative sequence networks are connected in parallel | |
7. |
A sustained three phase fault occurs in the power system shown in the figure. The current and voltage phasors during the fault (on a common reference), after the natural transients have died down, are also shown. Where is the fault located? |
A. | Point P |
B. | Point Q |
C. | Point R |
D. | Point S |
Answer» C. Point R | |
8. |
At the terminal of a 3ϕ, 6.6 kV, 10 MVA alternator, a load R = 200 Ω is connected between two phases, and other phase is kept open. The sequence impedance of the alternator is Z1 = Z2 = j 5Ω and Z0 = j2Ω. What is the current through the load resistance? |
A. | 50 A |
B. | 60 A |
C. | 75 A |
D. | 32 A |
Answer» E. | |