In a factory, a three-phase, 4-kV, 400-kVA synchronous machine is installed along with other induction motors. The following are the loads on the machine:(i) Induction motors: 500 kVA at 0.8 power factor lagging(ii) Synchronous motor: 300 kVA at unity power factorDetermine the overall power factor of the factory loads.

A. \(\frac{7}{\sqrt{58}}\) lagging
B. \(\frac{7}{\sqrt{58}}\) leading
C. \(\frac{9}{\sqrt{58}}\) leading
D. \(\frac{9}{\sqrt{58}}\) lagging
Answer» B. \(\frac{7}{\sqrt{58}}\) leading