Exhaust gases (c P = 1.12 k J/kg K) flowing through a tubular heat exchanger at the rate of 1200 kg/hr are cooled from 400 degree Celsius to 120 degree Celsius. This cooling is affected by water (c P = 4.18 k J/kg K) that enters the system at 10 degree Celsius at the rate of 1500 kg/hr. If the overall heat transfer coefficient is 500 k J/m² hr degree, what heat exchanger area is required to handle the load for parallel flow arrangement? |
| A. | 7.547 m² |
| B. | 6.547 m² |
| C. | 5.547 m² |
| D. | 4.547 m² |
| Answer» E. | |