| 1. |
A wind brace is to be provided between two columns spaced at 5 m, at an inclination of 30° with the horizontal, to resist a tension of 320 kN developed by a wind force. The effective area required will be nearly (considering 150 N/mm2 as a relevant factor) |
| A. | 1670 mm2 |
| B. | 1640 mm2 |
| C. | 1600 mm2 |
| D. | 1570 mm2 |
| Answer» D. 1570 mm2 | |