A wattmeter reads 10 kW, when its current coil is connected in R phase and the potential coil is connected across R and neutral of a balanced 400 V (RYB sequence) supply. The line current is 54 A. If the potential coil reconnected across B-Y phases with the current coil in R phase, the new reading of the wattmeter will be nearly |
A. | 10 kW |
B. | 13 kW |
C. | 16 kW |
D. | 19 kW |
Answer» C. 16 kW | |