1.

A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q consumed by the load are such that 1 kW ≤ P ≤ 2 kW and 1 kVAR ≤ Q ≤ 2 kVAR. A capacitor connected across the load for power factor correction generates 1 kVAR reactive power. The worst case power factor after power factor connection is

A. 0.447 lag
B. 0.707 lag
C. 0.894 lag
D. 1
Answer» C. 0.894 lag


Discussion

No Comment Found