1.

A domestic food freezer maintains a temperature of –15°C. The ambient air temperature is 30°C. If heat leaks into the freezer at the continuous rate of 1.75 kJ/s, the least power necessary to pump this heat out continuously will be nearly

A. 0.1 kW
B. 0.2 kW
C. 0.3 kW
D. 0.4 kW
Answer» D. 0.4 kW