A building has to be maintained at 21°C (dry bulb) and 14.5°C (wet bulb). The dew point temperature under these conditions is 10.17°C. The outside temperature is -23°C (dry bulb) and the internal and external surface heat transfer coefficients are 8 and 23 W/m2K respectively. If the building wall has a thermal conductivity of 1.2 W/mK, the minimum thickness (in m) of the wall required to prevent condensation is |
A. | 0.471 |
B. | 0.407 |
C. | 0.321 |
D. | 0.125 |
Answer» C. 0.321 | |