A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance is: |
| A. | 1 Ω |
| B. | 1.8 Ω |
| C. | 0.1 Ω |
| D. | 2.18 Ω |
| Answer» C. 0.1 Ω | |